"Roy J. Tellason" wrote to "ROBERT SAYRE" (26 Dec 02 12:06:02) --- on the topic of "HVDC Transmission Lines" RS> I always thought that the skin effect was negligible at low (60Hz) RS> frequencies. RJT> Same here. There's no doubt a formula for it in some book around RJT> here, but I have no idea which one, nor the inclination to dig it RJT> out at the moment... :-) You lazy sob!... From "MICROWAVE ENGINEEING" By David Pozar c 1990 Addison Wesley (P. 27) Skin depth (meters): ds=Sqrt(1/(PI*f*Mu0*sigma)) where sigma is conductivity of material in q. pi=3.141 f=60 Mu0=4*PI*1E-7 sigma for copper(Cu)=5.813E7 Skin depth for Cu at 60 HZ is 0.0085221 metres or 1/3 of an Inch. It's indeed negligible for house wiring but becomes significant for power transmission cables having 2 inches in diameter. Mike **** ... Now touch these wires to your tongue! --- Blue Wave/DOS v2.30* Origin: Juxtaposition BBS, Telnet:juxtaposition.dynip.com (1:167/133) SEEN-BY: 633/267 270 @PATH: 167/133 379/1 633/267 |
|