On Mon, 30 Jul 2018 18:47:14 +0100, Ahem A Rivet's Shot wrote:
> At domestic scale they make the householder immune to brown out and
> outages short enough not to drain them, proven repeatedly by everyone
> who has domestic power storage
er, AIUI the vast majority of domestic solar PV systems shut down
when the mains goes. They do *not* provide any autonomy.
> So for off-grid winter usage you need a system that produces enough
> energy for your needs at 20% of rated capacity,
So for 20 kWHr/day you need at *least* a 100kW rated system.
> The usual estimate for off-grid usage is at least five days storage.
1 kW @ 48 V = 20 A (ish). Total battery capacity 20 * (5 * 24) =
2,400 AHr.
>>> A few hours storage (say ten to twenty kilowatt hours) and a few
>>> kilowatts peak of panel (just enough that the total collected
annually
>>> is close to the total used annually)
"a few kilowatts peak"? Do the maths ... see above ... 20 kWHr/day
at 20% means a 100kW peak array.
--
Cheers
Dave.