Hi Mike
On (27 Jan 98) MIKE ROSS wrote to Alec Cameron...
MR> For this sort of mod I'd certainly have a master electrician do the
ork.
MR> Principally for the insurance concerns as you very wisely mention.
AC> Incidentally, you are unlikely to own enough generator capacity to
AC> allow an *Automatic* transfer. Make it non- auto, and invoke a Manual
AC> change AFTER turning off the electric cooker, dishwasher etc which
AC> might otherwise overload your generator.
Another thing........ AC motors require typically, from 8 to 12 times full
rated current, while accelerating from rest. That is often beyond the
capability of a small generator. For example, it is *very* improbable that
a 4HP petrol gen set, would be able to run a 2HP elec motor.
MR> Thanks for the really thoughtful straight thinking, Alec.
Well, I was a part time polytechnic teacher for 22 years. It's hard
o
shake those bad old habits ;-)
Cheers..........ALEC