> When a battery is a long time on preset float voltage a cell [or cells]
> behaves as the runt in the family, and its terminal voltage becomes
> a little
> suppressed. This automatically causes the charger to pump more amps
> and the healthy cells in the same battery oblige by raising v a bit, but
> still ahead of the runt, and the charger current self limits to a small
> amps value.
>
> In time a survey of that battery with a voltmeter, may show cell
> voltages like:
>
> 2.15 2.45 2.45 2.45 2.40 2.60. Total, 14.50v
Exactly what that KW Battery book explained.
I've found that my big RV/trolling batteries on the UPSs here don't seem to
hold up at all well. IE: a couple of years and they're done. It finally
dawned on me the the charger in the UPS is voltage limited to a low enough
value that the batteries will have to be equalized now and then.
I've gotten into the habit of load-testing the batteries, then charging them
at 5 amps for 5 hours, once per month or so. There's a log sheet hanging on
the wall for recording the CCA values indicated by the tester alongside the
date.
Interestingly enough, the gel-cell type batteries that are OEM in those UPSs
don't seem to need this treatment to hold up for several years. They'll
usually go 3-5 years without replacment.