>BB> I just went down and got me some of those great big binding
>BB> posts and drilled me two holes in the back wall of the UPS near
>BB> the upper right hand corner just above the top level of the 4
>BB> gel cells it cane with.
>
> This one's got two gels in there, and I don't know if there's
> enough room for a pair of those binding posts, it's really a pretty
> small case.
Roy,
I have 2 Topaz UPSs, both bought with bad batteries. One is 800VA, the other
1000VA, and they used a pair of 12 Volt batteries about the size of that in a
small garden tractor. I removed them and installed binding posts like Bill
did with his, using welding cable to connect each to a pair of 12 Volt
RV/Trolling batteries.
I used "arch punches" to make insulating washers from a plastic jug, and
1/4-20 brass bolts for the binding posts. There's 3 insulating washers per
post, 2 large ones about 1" dia. and a small one that's about 3/8" O.D. X
1/4" I.D. The I ended up with: the bolt, the lug on the wire, a large metal
washer, large insulating washer, the back panel of the UPS, the small
insulating washer, large insulating washer, large metal washer, and 1/4-20
nut in a stack. Install the wire with a 1/4-20 wingnut to make the
nnection.
As Bill pointed out, the charging is very slow, being limited to about 1 Amp
max. I think these are 105 AH batteries, so it could take 3 or 4 days to
charge them if they were "dead". Not a big deal for me, as we seldom get
outages that last more than a few seconds. The one fly in the ointment has
been relatively short battery life, they seem to only last 3 years or so. I
think that's due to their never getting an equalizing charge, so I've started
doing that on a farily regular basis. Every month or 2, I hit them with 5
amps continously for 5 or 6 hours.